Fig. 6.1 shows part of a mains circuit that includes three lamps and a heater. rating = 5 A live heating circuit fuse lighting circuit fuse heater neutral lamp type P lamp type P lamp type Q [Figure 6.1]
- (a)The mains voltage is 230 V, and the power of the heater is 2000 W. There is a 5A fuse in the lighting circuit. Four fuses of different ratings are available for use in the heating circuit as shown in the list. Underline the most suitable fuse value for the heating circuit fuse, and explain your choice. Your answer must include a calculation. available fuses: 5 A 8 A 13 A 30 A calculation explanation[3]
- (b)Describe what happens to a fuse when the current is too large.[1]
- (c)(i)Table 6.1 shows the current in lamps of type P and type Q when connected to the mains supply. Table 6.1 lamp type current/A P 0.26 Q 0.43 Calculate the current in the lighting circuit fuse when all three lamps are switched on. current = ....................................................A[1]
- (c)(ii)The rating for the lighting circuit fuse in Fig. 6.1 is 5A. The lamp of type Q is removed from the circuit. Calculate the maximum number of additional lamps of type P that can now be connected in parallel to the lighting circuit. number of additional lamps = ....................................................[1]
- (d)In some houses the lighting circuit is protected by a trip switch (circuit breaker) instead of a fuse. State two advantages of using a trip switch rather than a fuse. 1 2[2]
This question uses a diagram from the original paper, which isn't shown here. Open the full paper from the past papers archive to see it.
Mark scheme
Marking points from the official mark scheme (May/June 2025). The mark or mark type is shown in brackets.
- [1] (a) (I) = P / V or 2000 / 230 or 8.7 (A)
- [1] (a) fuse rating 13 A underlined or circled
- [1] (a) The fuse rating needs to be the lowest value above / slightly larger than the normal current / 8.7 A or 5/8 A fuse blows under normal operation / 8.7 A or 30 A fuse may not blow / heater or circuit damaged if fault or current larger than normal 8.7 A
- [1] (b) fuse melts / blows / or cuts off current / circuit
- [1] (c)(i) 0.95 (A)
- [1] (c)(ii) 17
- [2] (d) Any two from: (trip switches can / are) be reset / used more than once; faster acting / turns off immediately; more sensitive; be tested without replacement; have an external indication that they are working; can trip on difference in live and neutral currents